Question 8

What is the calculation for the desired attenuation factor for shielding material?

Options:

A.

A = 20 log (M / R)

Where

A is Attenuation

M is the maximum acceptable value

R is the real value measured

B.

A = M / R

Where

C.

A is Attenuation

M is the maximum acceptable value

R is the real value measured

D.

A = 20 log (R / M)

Where

A is Attenuation

R is the real value measured

M is the maximum acceptable value

E.

You do not have to calculate the attenuation factor for shielding material as it always has the same attenuation

Discussion
Syeda
I passed, Thank you Cramkey for your precious Dumps.
Stella May 2, 2026
That's great. I think I'll give Cramkey Dumps a try.
Norah
Cramkey is highly recommended.
Zayan May 12, 2026
Definitely. If you're looking for a reliable and effective study resource, look no further than Cramkey Dumps. They're simply wonderful!
Laila
They're such a great resource for anyone who wants to improve their exam results. I used these dumps and passed my exam!! Happy customer, always prefer. Yes, same questions as above I know you guys are perfect.
Keira May 22, 2026
100% right….And they're so affordable too. It's amazing how much value you get for the price.
Rae
I tried using Cramkey dumps for my recent certification exam and I found them to be more accurate and up-to-date compared to other dumps I've seen. Passed the exam with wonderful score.
Rayyan May 25, 2026
I see your point. Thanks for sharing your thoughts. I might give it a try for my next certification exam.
Stefan
Thank you so much Cramkey I passed my exam today due to your highly up to date dumps.
Ocean May 8, 2026
Agree….Cramkey Dumps are constantly updated based on changes in the exams. They also have a team of experts who regularly review the materials to ensure their accuracy and relevance. This way, you can be sure you're studying the most up-to-date information available.
Question 9

You need to determine the strategy for the cooling audit. All the servers are based on a front-to-rear (F-R) airflow design.

Which location for the temperature/humidity measurement should you recommend for the audit?

Options:

A.

At the back/rear of the server at 50 mm/2 inch

B.

At 1.5 meters/5 feet above the floor in the middle of the cold aisle

C.

At the front/intake of the server at 50 mm/2 inch

D.

At 1.5 meters/5 feet above the floor in the middle of the hot aisle

Discussion
Question 10

A customer requires THDi from the UPS not to exceed 3% and wants high efficiency. The UPS has a 6-pulse SCR/thyristor rectifier and is loaded ~80%. Many ICT changes are expected in the next 3 years. What should you recommend?

Options:

A.

Nothing; the UPS will keep THDi at the right levels

B.

Install a passive harmonic filter on the UPS

C.

Install an active harmonic filter on the UPS

D.

Install an isolation transformer rated K13 or K20

Discussion
Question 11

What is the minimum requirement for the power feeds to the building for a Rated-3 data center based on the ANSI/TIA-942 standard?

Options:

A.

Two feeds coming from two different substations, one power company is not acceptable

B.

Two feeds coming from two different substations, one power company is acceptable

C.

Two feeds entering the data center building from one substation

D.

One feed from one substation split over two separated distribution boards in separate rooms

Discussion